another cooker circuit question.

Home Forums Public Support Forums Help And Support Cooker And Oven Forum another cooker circuit question.

Viewing 2 posts - 1 through 2 (of 2 total)
  • Author
    Posts
  • #10725
    admin
    Keymaster

    Hi,

    our currect cook er cicuit is 30A. We have just ordered a boch single oven + bosch integrated microwave/combi oven. Looking on the Bosch website it appears the ratings are 20A for the cooker, 16A for he combi. Does this mean we will need another circuit installed fro the combi?

    Cheers

    #141678
    Graeme
    Participant

    Re: another cooker circuit question.

    If your supply cable is 6mm, it is possible to replace the 30A fuse or trip with a 45A one. The safest way to connect the appliances is to feed them both via 20A trips fed from the 45A supply. Having said that, you will be well advised to consult a local electrician who can check your circuit to see if there are any other reasons to prevent this being done. No short cuts to safety !!