APM6724 DIPLOMAT FRIDGE

Viewing 2 posts - 1 through 2 (of 2 total)
  • Author
    Posts
  • #28290
    alro
    Participant

    Hi Gents
    APM6724 not getting cold enough bypassed stat and back wall freezes all over plate evap but if i refit stat it only freezes about 2 or 3 inches down back wall,stat switches off comp any ideas
    do you have the same back pressure on r600 gas filled systems as r134a and r12 just another question for somebody in the know
    cheers alro

    #217681
    subs
    Participant

    Re: APM6724 DIPLOMAT FRIDGE

    I would think its a faulty stat, seeing as you get a fully frosted evaporator when you by pass it.

    R600 is normally slightly lower than R134 and R12.

    Subs