  • #49951
    Vince007
    Participant

    Hi, Does anyone know what amperage supply this cooker requires, 13, 16 or 30? Thank you. Vince

    #302837
    don
    Moderator

    Re: Hygena Turbo EVP302 / 335962 2.5kW

    Hi Vince007

    Can`t find that model no. listed i`m afraid., If it`s a single fan oven with grill it should be okay on the 13A circuit. If it`s a double oven then the thirty amp circuit should be used.

    What`s the total kw rating on the information plate?

    Don 🙂

    #302838
    Vince007
    Participant

    Re: Hygena Turbo EVP302 / 335962 2.5kW

    Hi Don. It is 2.5KW.
    Thanks
    Vince

    #302839
    don
    Moderator

    Re: Hygena Turbo EVP302 / 335962 2.5kW

    In that case as it`s only 10.41 amps the 13A circuit is fine.

    Don 🙂