Hygena Turbo EVP302 / 335962 2.5kW Home › Forums › Public Support Forums › Spare Parts Help › Hygena Turbo EVP302 / 335962 2.5kW This topic has 3 replies, 2 voices, and was last updated 16 years, 5 months ago by Vince007. Viewing 4 posts - 1 through 4 (of 4 total) Author Posts November 7, 2009 at 8:38 am #49951 Vince007Participant Hi, Does anyone know what amperage supply this cooker requires, 13, 16 or 30? Thank you. Vince November 7, 2009 at 9:00 am #302837 donModerator Re: Hygena Turbo EVP302 / 335962 2.5kW Hi Vince007 Can`t find that model no. listed i`m afraid., If it`s a single fan oven with grill it should be okay on the 13A circuit. If it`s a double oven then the thirty amp circuit should be used. What`s the total kw rating on the information plate? Don 🙂 November 7, 2009 at 9:24 am #302838 Vince007Participant Re: Hygena Turbo EVP302 / 335962 2.5kW Hi Don. It is 2.5KW. Thanks Vince November 7, 2009 at 9:53 am #302839 donModerator Re: Hygena Turbo EVP302 / 335962 2.5kW In that case as it`s only 10.41 amps the 13A circuit is fine. Don 🙂 Author Posts Viewing 4 posts - 1 through 4 (of 4 total) You must be logged in to reply to this topic. Log In Username: Password: Keep me signed in Log In