Ideal HE30 Boiler with LF fault

Home Forums Trade Technical & Spare Parts Forums Trade Technical Enquiries Ideal HE30 Boiler with LF fault

Viewing 6 posts - 1 through 6 (of 6 total)
  • Author
    Posts
  • #93323
    roytheboy
    Participant

    Hi
    Ive been to an Ideal HE30 boiler today with fault LF showing.
    After checking the flame sensing probe, the dc voltage at the gas control valve. the ignition system the fault is still there.
    I took off the tube from the gas control valve to the casing, there was water in it.
    I cleared the water and it started working again, for about 6 hours, then the fault came back.
    I returned this evening and although there was no water in the tube, when I sucked the tube while still attached to the gas valve some more water came out and the boiler is working again, for now.
    Does anyone have any ideas on what is happening and what needs to done to sort it.
    Cheers
    Roy

    #453937
    kaibart
    Moderator

    Re: Ideal HE30 Boiler with LF fault

    Firstly are you gas safe and qualified to work on boilers

    #453938
    roytheboy
    Participant

    Re: Ideal HE30 Boiler with LF fault

    yes on both accounts

    #453939
    kaibart
    Moderator

    Re: Ideal HE30 Boiler with LF fault

    Well it sound like a ignition fault soit needs to be stripped down and cleaned the dirt and carbon builds up around the ignition and flame sensor underneath so good clean should sort this Kai

    #453940
    roytheboy
    Participant

    Re: Ideal HE30 Boiler with LF fault

    Thanks for the reply.
    I’ll give it a good clean out and let you know.

    #453941
    Martin
    Participant

    Re: Ideal HE30 Boiler with LF fault

    It’s more than a simple ignition fault I suspect. Having to drain the water suggests a condensate drainage issue, frozen pipe outside maybe? Have you checked the user manual I wonder?

    Here’s a copy……

    http://idealboilers.com/uploads/documen … -guide.pdf