Re: insulation test
waters wrote:is a motor will pass at 4m but how long will it last if most i test are 20m including new ones
The thing to bear in mind especially with motor insulation and machines these days with electronic controls. Is that any high insulation reading (5 to 10 meg for example) can see the circuit board go up in smoke. 🙁
So if you are reconning machines and putting them out with any sort of guarantee, I would suggest failing any motor with an insulation less than 20 meg. And take the motor apart and clean it! 😉