insulation testing

Viewing 7 posts - 1 through 7 (of 7 total)
  • Author
    Posts
  • #69284
    dealdd
    Participant

    i have a cooker which is in total rated over 3kw and when i do insulation test it comes to 0.48mohm but only reads that from the grill element. Does any one know if the 0.3mohm test on class 1 heating appliences is the total of the cooker or can i do it on individual elements??

    #374229
    Martin
    Participant

    Re: insulation testing

    dealdd wrote:Does any one know if the 0.3mohm test on class 1 heating appliences is the total of the cooker

    0.3Mohm is the TOTAL for Class 1 (cooker) based on a standard insulation test @ 500vDC.

    #374230
    dealdd
    Participant

    Re: insulation testing

    is that the case if the cooker is over 3 kilo watts??

    i thought it went to 1 mohm if over 3kw.

    what i want to know is this total of whole cooker or individual elements

    #374231
    Martin
    Participant

    insulation testing

    Did you note that I highlighted the word Total in my last post?


    Sent from my iPad

    #374232
    dealdd
    Participant

    Re: insulation testing

    yes. but this is a cooker over 3kw which i think has to be over 1 Mohm? i was wondering if this was still total

    #374233
    RocketMan
    Participant

    Re: insulation testing

    I can’t access my code of practice book at the moment but like Martin, I’m positive it’s for the whole appliance.
    Look at it from this point of view: If the customer has the grill in use, and then they put the fan oven on, that’s probably over 3KW. 😉

    #374234
    dealdd
    Participant

    Re: insulation testing

    ok cheers best to be safe than sorry