December 22, 2019 at 12:17 pm #96924
itm60
ParticipantI’m looking for electrical cable to connect a double oven to a 32A supply. The oven is rated at 4kW. Can anyone advise on whether this would be suitable?
https://www.screwfix.com/p/prysmian-6242y-twin-earth-cable-6mm-x-10m-grey/29733
PRYSMIAN 6242Y TWIN & EARTH CABLE 6MM² X 10M GREY [TABLE]
[TR]
SPECIFICATION [/TR]
[TR]
[TD]Brand[/TD]
[TD]Prysmian[/TD]
[/TR]
[TR]
[TD]Cable Code[/TD]
[TD]6242Y[/TD]
[/TR]
[TR]
[TD]Cable End Type[/TD]
[TD]Bare[/TD]
[/TR]
[TR]
[TD]Cable Length[/TD]
[TD]10 m[/TD]
[/TR]
[TR]
[TD]Cable Product Type[/TD]
[TD]Twin & Earth[/TD]
[/TR]
[TR]
[TD]Cable Profile[/TD]
[TD]Flat[/TD]
[/TR]
[TR]
[TD]Cable Voltage Rating[/TD]
[TD]300/500 V[/TD]
[/TR]
[TR]
[TD]CE Standard (Tested to EN…)[/TD]
[TD]BS 6004.[/TD]
[/TR]
[TR]
[TD]Coil or Drum[/TD]
[TD]Coil[/TD]
[/TR]
[TR]
[TD]Colour[/TD]
[TD]Grey[/TD]
[/TR]
[TR]
[TD]Conductor Area[/TD]
[TD]6 mm²[/TD]
[/TR]
[TR]
[TD]External Diameter[/TD]
[TD]13.1 mm[/TD]
[/TR]
[TR]
[TD]Indoor/Outdoor Usage[/TD]
[TD]Indoor[/TD]
[/TR]
[TR]
[TD]Manufacturer Guarantee[/TD]
[TD]1 Year Guarantee[/TD]
[/TR]
[TR]
[TD]Maximum Operating Temperature[/TD]
[TD]70 °C[/TD]
[/TR]
[TR]
[TD]Minimum Operating Temperature[/TD]
[TD]-15 °C[/TD]
[/TR]
[TR]
[TD]Model No[/TD]
[TD]20147221[/TD]
[/TR]
[TR]
[TD]No. of Cable Cores[/TD]
[TD]2-Core[/TD]
[/TR]
[TR]
[TD]No. of Strands Per Core[/TD]
[TD]7 Strands Per Core[/TD]
[/TR]
[TR]
[TD]Pack Size[/TD]
[TD]1[/TD]
[/TR]
[TR]
[TD]Parent Colour[/TD]
[TD]Grey[/TD]
[/TR]
[TR]
[TD]Pieces in Pack/Case[/TD]
[TD]1[/TD]
[/TR]
[TR]
[TD]Product Type[/TD]
[TD]PVC Flat Wiring Cable[/TD]
[/TR]
[TR]
[TD]Sheath Colour[/TD]
[TD]Grey[/TD]
[/TR]
[TR]
[TD]Supplier Manufacturer Helpline[/TD]
[TD]08457 678 345[/TD]
[/TR]
[/TABLE]It’s longer than I need, but the shortest that I could find in Screwfix!
December 22, 2019 at 1:51 pm #465414Specialist01269
ParticipantHi: 6mm is more than adequate for what you need.
December 22, 2019 at 2:40 pm #465415electrofix
Moderatoras above 6mm is more than adequate
at 4Kw your oven only draws a max of just under 17A so is about 50{e5d1b7155a01ef1f3b9c9968eaba33524ee81600d00d4be2b4d93ac2e58cec2d} of the mcb rating
If you have a tool station near your screwfix they are slightly cheaper on the cable
also if you can find a small local electrical wholesaler they can cut cable to length
Dave
December 22, 2019 at 3:36 pm #465416Specialist01269
ParticipantTLC still do cut to length cable, but not open on Sunday.
December 23, 2019 at 9:51 am #465417itm60
ParticipantThanks. Is there any reason that I might use heat resistant cable, which someone has suggested to me?
December 23, 2019 at 10:01 am #465418itm60
Participant…and would 2.5mm cable suffice? Someone has recommended this:
https://www.screwfix.com/p/nexans-heat-resistant-flex-3183tq-3-core-2-5mm-5m-white/8869tDecember 23, 2019 at 10:21 am #465419electrofix
Moderatoryou can use heat resisting if you want to but its not necessary with an oven. Its more important with a hob where the terminal block is nearer the elements
Dave
December 23, 2019 at 10:27 am #465420Specialist01269
ParticipantHeat resistant would be fine and 2.5mm would be ok as it’s rated at 25a, your 4Kw oven should draw a maximum of just under 17a at full power. If using 2.5 flexible then make sure that you get a good wrap around the terminal screw or double it back under the connection clamp and twist the strands together well.
-