Open Neutral on the socket ring

Home Forums Public Support Forums General Enquiries And Questions Open Neutral on the socket ring

Viewing 6 posts - 1 through 6 (of 6 total)
  • Author
    Posts
  • #103242
    Raovencleaning
    Participant

    Hi all, just checking if a open neutral detected on the kitchen sockets would cause the range cooker to trip the power?
    im pretty confident it would be the problem.

    But I’d appreciate an experienced opinion.

    Cheers
    Rob

    #492318
    electrofix
    Moderator

    if they are on different circuits they cant affect one another

    most of the time a cooker is on its own circuit

    Dave

    #492319
    Raovencleaning
    Participant

    Good point, I checked everything on the range but its tripping the circuit on both ovens, grill and induction hob (when turned on individually).
    could it be thermal cut switches?

    #492320
    Raovencleaning
    Participant

    Although I did test them and all low readings so ok.

    #492321
    electrofix
    Moderator

    ok we need to know whats tripping

    RCD that detects earth faults ( look for the test button )

    MCB that act like a fuse and detects over current faults

    or the latest trips that combine both RCBO

    Dave

    #492322
    Raovencleaning
    Participant

    Cheers Dave I’ll look into it